geoffsnook Member Since: 19 Nov 2016 Location: cardiff Posts: 1702 |
So could you let me know how to change the readings on the idd as mine reads in kpa or do i need to connect gap |
||
Sun Jun 04 2017 1:05pm |
|
Sharpy1980 Member Since: 24 Sep 2016 Location: Kent Posts: 98 |
From memory I'm pretty sure that when you go into the live values there are 3 options and you want "units" and then you choose which one you want Clickadeeclick |
||
Sun Jun 04 2017 9:13pm |
|
geoffsnook Member Since: 19 Nov 2016 Location: cardiff Posts: 1702 |
Hi spent all day monday on this evaporated gas what gas i might say absolutely nothing in there so started with the uv light (no nitrogen) spent about 2 and a half hours looking everywhere no green dye anywhere to be seen but found quite a lot around the Schraeder valves so after a bit of discussion and searching we decided to refill so first we vacuumed for 55 mins and refilled and so far the system has stayed up and running so thats 2 days which is a lot longer than before and my IID tells me that i have between 5 bar and 16 bar of pressure with an outside temp of between 10 and 16 degrees so i hope it was just that the valves were not seated properly does the pressure sound right though as it seems to rise and fall a fair bit when on auto |
||
Wed Jun 07 2017 7:32am |
|
GodivaNige Member Since: 14 May 2016 Location: Warwickshire Posts: 420 |
Good that you have determined the issue was a loss of refrigerant and applying a decent vacuum after a full search for a leak is the way to go. However, a system pressure up to 16 bar is too high for R134a. Is the viscous fan duty cutting in ok?
|
||
Wed Jun 07 2017 3:52pm |
|
geoffsnook Member Since: 19 Nov 2016 Location: cardiff Posts: 1702 |
Thanks for that I only have a non Bluetooth Iid tool so I only can see the system pressure I assume that it is the high side it reads I only saw 16 bar once when I started it this morning it was at about 3 bar and rose to about 8-10bar after a few mins and was working well when temp was about 10-11 degrees |
||
Wed Jun 07 2017 4:22pm |
|
|